Posts: 4,773
You can run the mast ground as far as needed. Use at least a #10 AWG copper conductor. (#8 & #6 are larger and can be used as well... they're going to be more expensive options as a result.)

Hopefully, the existing satellite system coax is already grounded, ideally within a few feet of where it enters the building. If not, then the ideal solution is to locate the grounding block outside, close to the electrical service ground, thus allowing you to use a short length (less than 10' total) of #10 AWG copper to connect the grounding block to the existing electrical service ground. I would even go so far as to run coax from the antenna to the area near the electrical service... coax is less expensive and easier to work with than #6 copper. If you choose to install a new ground rod close to the antenna, it should be bonded to the existing electrical service ground with no less than a #6 AWG copper conductor.

The multi-switch is a satellite system only device. It needs to be removed and replaced with a splitter.
__________________
If the well is dry and you don't see rain on the horizon, you'll need to dig the hole deeper. (If the antenna can't get the job done, an amp won't fix it.)