Originally Posted by nickgalliart
Thanks for the reply!
The pole for the antenna is in the ground about 20 feet away from the house's electrical service ground. If I use a grounding device like what is in your profile picture, should I just run a separate AWG wire to the house's electrical service ground?
|
That's what I have done with my masts; A dedicated bonding connection from the mast to the existing electrical service grounding system using #10 AWG. I treat the coax shield bonding as a separate, but equally important connection.
__________________
If the well is dry and you don't see rain on the horizon, you'll need to dig the hole deeper. (If the antenna can't get the job done, an amp won't fix it.)